  1. In the two-wattmeter method of measuring power in a balanced three-phase circuit, one wattmeter shows zero and the other positive maximum. The load power factor is _________
    1. 0.5
    2. 0.2
    3. 1.2
    4. 1.5
Correct Option: A

The wattmeters reading is proportional to cos (30 + φ)
Then other is proportional cos (30 – φ)
Thus whenever load p.f. angle φ becomes 60°, one of the wattmeters would read zero.
Hence for the given condition load load
p.ƒ = cos 60° = 0.5