  1. Given the maximum efficiency of a transformer of a 500 kVA, 3300/500V, 50 Hz single-phase transformer is 97% and occurs at 3/4 of full-load, unity power factor. If the impedance is 10%, the regulation at full-load, power factor 0.8 lagging will be _____ % .
    1. 8.25%
    2. 17.52%
    3. 7.52%
    4. 10.52%
Correct Option: C

η = 0.97 = 500 ×
3
× 1
4
500 ×
3
+ Pcore + Pcu ×
9
416

⇒ Pcore + Pcu ×
9
= 11.60
16

⇒ Pcu = 10.31 kW (at full-load)
∴ re (p.u.) =
Pcu
=
10.31
= 0.02062
kVArated500

xe (p.u.) = √Ze² - re²
= √0.1² - (0.02062)² = 0.0978
∴ Regulation = re cos θ + xe sin θ
= 0.02062 × 0.8 + 0.0978 × 0.6 = 7.52%